We can find no reference either and worse, we know nothing of the product line you are referencing. For example, is this bare conductor cabled with insulated conductors? I'm afraid you make it very difficult for us but we do suggest you carefully review the Doha Cables catalog at
www.elsewedyelectric.com/Catalogs/Doha%20Cables.pdf Within this catalog, you will find the method of calculation of Cable Short Circuit Capacity, the properties of Annealed and Hard Drawn Copper and references for a number of IEC documents including:
60028 - International standard for resistance of copper.
60949 - Calculation of thermally permissible short circuits, taking into account non-adiabatic heating effects.
60986 - Guide to the short circuit temperature limits of electric cables with a rated voltage of 1.8/3 (3.6 kV) to 18/30 (36 kV).
61089 - Round wire concentric lay overhead electrical stranded conductors.
61597 - Overhead electrical conductors - Calculation methods for stranded bare conductors.
61443 - Short circuit temperature limits of electrical cables with rated voltages above 30 kV (Um=36 kV).
There are also references for British Specifications:
BS 7884 - Copper and copper -cadmium stranded conductors for overhead electric traction and power transmission systems.
BS EN 13602 - Copper and copper alloys - Drawn round copper wire for the manufacture of electrical conductors.
BS EN 50182 - Conductors for overhead lines - Round wire concentric lay stranded conductors.
The key to the information you are looking for may reside somewhere in these specifications but you are going to have to do some studying to find it. Good luck.