Hello again,
Although you are pretty well next to the lowest voltage of triple layer low voltage power cable, many higher voltage power cable companies work with a maximum internal methane pressure "p" of 0.2 kg/ cm*2 and graphs for mathematical degassing times are developed on the basis of that final internal methane pressure and the total thickness all three of the XLPE layers. This pressure limit was experimentally determined to give not more than 1 mm cable jacket swell and that was found to be adequate.
If you use woven type semiconducting tapes on top of the conductor, there should be no retarding of the methane gas coming out of solution so the degassing times should not change.
If you place air tight end caps on the cables that have not been properly degassed and and leave them outside, a methane internal/external pressure equilibrium will be formed and the cables will not be properly degassed.
If your problem is indeed methane coming out of the cables, collect the bubbles and have your laboratory determine if you have actually collected methane. Be careful of small explosions however. The chemists will know how to handle this properly.
Then you may wish to talk with Maillefer some more.