Hello There Chimiza,
There are a number of factors that affect the ovality of the insulation when the thicknesses are large. We recommend the following for good processing:
- The catenary angle should be fairly high - Say 18 to 25 degrees. From an insulation sag perspective of course, the higher the angle, the better.
- A triple crosshead is preferred along with a conductor preheater.
- The plastic temperatures should be as low as possible in the extruders.
- The profile temperature in the CV tube should not be excessively high.
- Rotating the cable in the CV tube will reduce insulation sag.
- An X-ray diameter and eccentricity monitor at the splice box is recommended.
- A secondary eccentricity monitor at the exit of the pull out capstan is also recommended to verify there has been no insulation sag.
- Gradient cooling is preferred to lessen shrinkback.
As far as an actual CV tube thermal profile is concerned, use the computer program you got with your CV line. Check with your supplier for program upgrades or newer versions.
There is significant processing experience to be learned and documented as the wall thicknesses increase. We wish you good luck in this venture.
Kindest regards,
Peter J. Stewart-Hay
Principal
Stewart-Hay Associates